The interesting thing about the EPO and data centers is it
wasn't 
orginally for life-safety, but came out of a recommendation
by IBM
to the NFPA for property protection.

But like many things, the original reasoning been lost to
history, and 
the codes grew in different ways.


http://www.dat
acenterknowledge.com/archives/2007/May/07/averting_disaster_
with_the_epo_button.html

   The history of the emergency power off switch dates back
to 1959, when a
   fire in the Air Force's statistical division in the
Pentagon caused $6.9
   million in property damage and destroyed three IBM
mainframe computers.
   "Nothing gets the government.s attention like
something that happens to
   government," said Sawyer. The National Fire
Protection Agency (NFPA) was
   tasked to develop rules to address fire risks in IT
environments.


Sometimes you need to revisit the rules.  For example, for
folks
thought having automatic water sprinklers in data centers
was a bad thing. 
Slowly folks have started to rethink it, and now automatic
sprinklers are
found in more data centers.  I don't have hard data, but my
experience
is there have been fewer outages from accidental sprinkler
discharges
than from accidental EPO activations.

Re: History of the EPO (Emergency Power Off)
country flaguser name
United States
2007-07-25 22:22:49
At 08:10 PM 7/25/2007, Sean Donelan wrote:
>Sometimes you need to revisit the rules.  For example,
for folks
>thought having automatic water sprinklers in data
centers was a bad 
>thing. Slowly folks have started to rethink it, and now
automatic 
>sprinklers are
>found in more data centers.  I don't have hard data, but
my experience
>is there have been fewer outages from accidental
sprinkler discharges
>than from accidental EPO activations.

There was an interesting study conducted by the US Air Force
about 
fires and other failure modes in computing facilities
protected with 
Halon/FM200/FE227 vs. dry pipe preaction. I know I saved the
PDF, but 
I can't seem to find it at the moment. If my memory is
correct, it 
boiled down to the fact that there had only been two fire
incidents 
at all US Air Force installations and both were due to
(surprise, 
surprise) human factors. One was a stray incendiary munition
which 
breached the datacenter and other was due to a Jet A fuel
spill and 
fire - which is odd because it is hard to ignite kero,
diesel, jet A 
without atomization. The point of the study was that there
was zero 
damage over a 30 year period from water based fire
protection systems 
and I suspect it was pretty handy to have sprinklers when
both 
datacenter fires happened. The munition breach of the
physical 
structure would have rendered any gas based fire suppression
system 
ineffective.

In theory, I'm not a big fan of EPOs due to the "Is
this the button 
to exit/open the door?" problem. One of our redundant
150KVA UPS 
units caught fire a couple years ago, the input breaker
became the 
EPO since the on-board front panel EPO was completely
ineffective 
(and it still would have been ineffective had it been
connected to an 
external EPO button.) That incident prompted a design change
in all 
of our new datacenter power systems since and all existing
systems 
were also updated. Now all UPS units have separate input and
bypass 
breakers and feeds. Previously we used a single feed, but
you can't 
isolate a burning UPS without dropping your attached load
when they 
share a single breaker and are tied together inside the unit
where 
the fire is happening. Having discrete A & B power
systems is also a 
very good thing!

Many years ago when we were much, much smaller, the EPO was
wired to 
a special EPO circuit breaker on the main panel which fed
the 
subpanel for the datacenter room. A short on that breaker
was like 
pressing the "test" switch on a GFCI breaker. Do
most people who do 
have functional (as opposed to decorative) EPO buttons have
them 
connected to the building/suite mains disconnect? or to the
output of 
your UPS units? to a special EPO panel which trips the EPO
cutoffs on 
other units?

-Robert


Tellurian Networks - Global Hosting Solutions Since 1995
http://www.tellurian.com
| 888-TELLURIAN | 973-300-9211
"Well done is better than well said." - Benjamin
Franklin


Re: History of the EPO (Emergency Power Off)
country flaguser name
United States
2007-07-25 23:23:26
From: "Sean Donelan" <seandonelan.com>
Subject: History of the EPO (Emergency Power Off)


>> The interesting thing about the EPO and data
centers is it wasn't
 orginally for life-safety, but came out of a recommendation
by IBM
 to the NFPA for property protection.<<

Fwiw, the EPO on  IBM's mainframes back in those days, had
to be -pulled- and had a mechanical 'latch' that kept it
from being 
pushed back in.  Took both hands to reset it.

--Michael


Re: History of the EPO (Emergency Power Off)
country flaguser name
United States
2007-07-26 14:47:58

When I was designing a sizeable machine room at BU I
remember getting
into a bit of a debate with someone from buildings because
they wanted
(I think the numbers are right) 140F sprinklers and I wanted
175F
sprinklers, images of an accidental sprinkler discharge
dancing in my
head (we had halon and all that, but 140F at the ceiling
didn't seem
all that high w/ all those big racks.)

     Me:  *I've* got over $2M in computers in that room!
     Him: *I've* got over $20M building around that room!
     Me:  You win!

-- 
        -Barry Shein

The World              | bzsTheWorld.com           | http://www.TheWorld.com
Purveyors to the Trade | Voice: 800-THE-WRLD        | Login:
Nationwide
Software Tool & Die    | Public Access Internet     |
SINCE 1989     *oo*

Re: History of the EPO (Emergency Power Off)
country flaguser name
United States
2007-07-26 23:22:26
 >
> Many years ago when we were much, much smaller, the EPO
was wired to a 
> special EPO circuit breaker on the main panel which fed
the subpanel for 
> the datacenter room. A short on that breaker was like
pressing the "test" 
> switch on a GFCI breaker. Do most people who do have
functional (as 
> opposed to decorative) EPO buttons have them connected
to the 
> building/suite mains disconnect? or to the output of
your UPS units? to a 
> special EPO panel which trips the EPO cutoffs on other
units?
>

I'd guess what you are describing is what is known as a
"SHUNT TRIP" coil in 
the large breaker you need to trip. This is a readily
available option even 
on relatively small breakers - just feed it power and it
trips the breaker.

However it does need seperate power run through the EPO
button and fed from 
a small dedicated 15 or 20AMP normal branch circuit
breaker.

Once the inspector has permanently departed, that little
breaker can be 
"accidentally" left tripped and then the EPO
function does not work - no 
"wiring/unwiring" skills needed.

Ususal issues of liability, so decide if/how to inform other
staff.
 