On 25 Mar 2008, at 09:11 , Dorn Hetzel wrote:

> It would sure be nice if along with choosing to order
servers with  
> DC or AC power inputs one could choose air or water
cooling.
>
> Or perhaps some non-conductive working fluid instead of
water.  That  
> might not carry quite as much heat as water, but it
would surely  
> carry more than air and if chosen correctly would have
more benign  
> results when the inevitable leaks and spills occur.

The conductivity of (ion-carrying) water seems like a
sensible thing  
to worry about. The other thing is its boiling point.

I presume that the fact that nobody ever brings that up
means it's a  
non-issue, but it'd be good to understand why.

Seems to me that any large-scale system designed to
distribute water  
for cooling has the potential for hot spots to appear, and
that any  
hot spot that approaches 100C is going to cause some
interesting  
problems.

Wouldn't some light mineral oil be a better option than
water?


Joe


Re: rack power question
country flaguser name
United States
2008-03-25 09:19:40
Dorn Hetzel wrote:
> Of course, my chemistry is a little rusty, so I'm not
sure about the 
> prospects for a non-toxic, non-flammable,
non-conductive substance with 
> workable fluid flow and heat transfer properties 

Mineral oil?  I'm not sure about the non-flammable part
though.  Not all 
oils burn but I'm not sure if mineral oil is one of them. 
It is used 
for immersion cooling though.

Justin


RE: rack power question
country flaguser name
United Kingdom
2008-03-25 10:06:35
While it has the potential to catch fire - it does however
work fine in my
car engine. 

-----Original Message-----
From: owner-nanogmerit.edu [mailto:owner-nanogmerit.edu] On Behalf Of
Justin Shore
Sent: 25 March 2008 14:20
To: Dorn Hetzel
Cc: nanog list
Subject: Re: rack power question


Dorn Hetzel wrote:
> Of course, my chemistry is a little rusty, so I'm not
sure about the 
> prospects for a non-toxic, non-flammable,
non-conductive substance 
> with workable fluid flow and heat transfer properties


Mineral oil?  I'm not sure about the non-flammable part
though.  Not all
oils burn but I'm not sure if mineral oil is one of them. 
It is used for
immersion cooling though.

Justin

RE: rack power question
country flaguser name
United States
2008-03-25 10:11:39
Well, seeing as that most pad mounted transformers use
mineral oil as a
heat transfer agent (in applications up to and exceeding
230kv), I don't
suspect it is of issue.

However, we've all seen nice transformer fires.


> -----Original Message-----
> From: owner-nanogmerit.edu [mailto:owner-nanogmerit.edu] On Behalf
Of
> Justin Shore
> Sent: Tuesday, March 25, 2008 10:20 AM
> To: Dorn Hetzel
> Cc: nanog list
> Subject: Re: rack power question
> 
> 
> Dorn Hetzel wrote:
> > Of course, my chemistry is a little rusty, so I'm
not sure about the
> > prospects for a non-toxic, non-flammable,
non-conductive substance
> with
> > workable fluid flow and heat transfer properties

> 
> Mineral oil?  I'm not sure about the non-flammable part
though.  Not
all
> oils burn but I'm not sure if mineral oil is one of
them.  It is used
> for immersion cooling though.
> 
> Justin

Re: rack power question
country flaguser name
United States
2008-03-25 10:15:36
Russia (or the USSR at that time) used to use liquid
graphite to cool their 
nuclear reactors, even thought it was flammable.... of
course that was what 
they were using in Chernobyl. 


-- 
Brian Raaen
Network Engineer
braaenzcorum.com

On Tuesday 25 March 2008, you wrote:
> 
> Dorn Hetzel wrote:
> > Of course, my chemistry is a little rusty, so I'm
not sure about the 
> > prospects for a non-toxic, non-flammable,
non-conductive substance with 
> > workable fluid flow and heat transfer properties

> 
> Mineral oil?  I'm not sure about the non-flammable part
though.  Not all 
> oils burn but I'm not sure if mineral oil is one of
them.  It is used 
> for immersion cooling though.
> 
> Justin
> 
>

Re: rack power question
user name
2008-03-25 10:16:27
Question: what worries you more, fire or leaks?

On Tue, Mar 25, 2008 at 3:06 PM, Ben Butler < ben.butlerc2internet.net">ben.butlerc2internet.net> wrote:

While it has the potential to catch fire - it does however work fine in my
car engine.

-----Original Message-----
From: owner-nanogmerit.edu">owner-nanogmerit.edu [mailto: owner-nanogmerit.edu">owner-nanogmerit.edu] On Behalf Of
Justin Shore
Sent: 25 March 2008 14:20
To: Dorn Hetzel
Cc: nanog list
Subject: Re: rack power question


Dorn Hetzel wrote:
&gt; Of course, my chemistry is a little rusty, so I'm not sure about the
> prospects for a non-toxic, non-flammable, non-conductive substance
> with workable fluid flow and heat transfer properties

Mineral oil?  I9;m not sure about the non-flammable part though.  Not all
oils burn but I'm not sure if mineral oil is one of them.  It is used for
immersion cooling though.

Justin


RE: rack power question
country flaguser name
United States
2008-03-25 10:47:38
I think the modern equivalent is HFE, manufactured by 3M;
HFE-7100 is
commonly used in the ATE industry for liquid cooling of test
heads.  It
is designed for very low temperatures (-135degC to 61degC)
so it might
not be suitable for general datacenter use.  HFE-7500 looks
like a
better fit. (-100degC to 130degC)



-----Original Message-----
From: owner-nanogmerit.edu [mailto:owner-nanogmerit.edu] On Behalf Of
Chris Adams
Sent: Tuesday, March 25, 2008 6:38 AM
To: nanog list
Subject: Re: rack power question


Once upon a time, Dorn Hetzel <dhetzelgmail.com> said:
> Of course, my chemistry is a little rusty, so I'm not
sure about the 
> prospects for a non-toxic, non-flammable,
non-conductive substance 
> with workable fluid flow and heat transfer properties


Fluorinert - it worked (more or less) for the Cray Triton.
--
Chris Adams <cmadamshiwaay.net>
Systems and Network Administrator - HiWAAY Internet Services
I don't
speak for anybody but myself - that's enough trouble.

Re: rack power question
country flaguser name
United States
2008-03-25 10:51:51

On Mar 25, 2008, at 11:15 AM, Brian Raaen wrote:
>
> Russia (or the USSR at that time) used to use liquid
graphite to  
> cool their
> nuclear reactors, even thought it was flammable.... of
course that  
> was what
> they were using in Chernobyl.
>

The RBMK-1000 used graphite for moderation and water for
cooling.

Regards
Marshall

>
> -- 
> Brian Raaen
> Network Engineer
> braaenzcorum.com
>
> On Tuesday 25 March 2008, you wrote:
>>
>> Dorn Hetzel wrote:
>>> Of course, my chemistry is a little rusty, so
I'm not sure about the
>>> prospects for a non-toxic, non-flammable,
non-conductive  
>>> substance with
>>> workable fluid flow and heat transfer
properties 
>>
>> Mineral oil?  I'm not sure about the non-flammable
part though.   
>> Not all
>> oils burn but I'm not sure if mineral oil is one of
them.  It is used
>> for immersion cooling though.
>>
>> Justin
>>
>>


RE: rack power question
country flaguser name
United States
2008-03-25 10:53:07

Dorn Hetzel wrote:
&gt; Of course, my chemistry is a little rusty, so I'm not sure about the
> prospects for a non-toxic, non-flammable, non-conductive substance
> with workable fluid flow and heat transfer properties

For some of us over-the-edge pc enthusiasts, we use a non-conductive heat transfer fluid for ‘water-cooling&#8217; our over-clocked cpus:

http://www.dangerden.com/store/home.php?cat=63. If you buy it in gallons, I’m sure you’ll get a better price.&nbsp; If I recall, conductivity is somewhat less than water, but still good enough to do the job.  I have a solution in place that has been running continuously for two or three years now.  By distributing the heat to larger slower fans, my room is quieter.&nbsp;  If I was really inclined, I could put the fans out my window and have practically dead silence, if it wasn’;t for the power supply fan.

 Another poster mentioned dripless quick-disconnects.&nbsp; They do exist.

RE: rack power question
country flaguser name
United Kingdom
2008-03-25 11:04:58
>  Or perhaps some non-conductive working fluid instead of water.&nbsp;  
>  That might not carry quite as much heat as water, but it would surely&nbsp; 
>  carry more than air and if chosen correctly would have more benign results&nbsp; 
>  when the inevitable leaks and spills occur.&nbsp; 
 
HCFC-123 is likely what would be used, which means that you would want to limit the amount of time that you spend inside&nbsp;the data center because, with the large ;number of connections in the facility, leaks will&nbsp;be inevitable and inhaling the gas causes liver damage.
 
Essentially, you are saying that we should get rid of chillers and turn the entire data center into a giant chiller. Instead of being a building with rooms and equipment, the data center becomes a machine and humans only venture inside when the machine is shut down for maintenance. 
 
>  Less practical but more fun to contemplate would be data centers pressurize 
>  with a working gas that offers better heat transfer than oxygen/nitrogen and no  
>  oxidation potential.  Airlocks and suits for the techs, but no fire worries ever.  
>  Heck, just close the room and inject liquid nitrogen under the raised floor to be  
>  scavenged overhead and re-compressed, chilled, liquefied and sent round again.&nbsp; 
> ; Reserve cooling for power outages is just huge dewars full of liquid nitrogen

 >  Not so serious today,
 
Why not? If you take your pressurized liquid nitrogen scenario and turn it inside out, then it might well be workable and there would&nbsp;be no need for suits. For instance,&nbsp;imagine a cylinder containing the liquid nitro cooling (liquid air might be cheaper)&nbsp;with devices attached all around like the petals on a flower. Each device has ;heat exchangers for cooling the hottest parts (CPUs) and the heat exchangers are attached to the cooling cylinder. With continued&nbsp;increase in density of cores, this could be feasible. In essence it would be a kind of blade server with the cooling and backplane in a central cylinder. Added benefits might come from supercooling the backplane.
 
Consider what is happening&nbsp;beyond the consumer dual and 8-core (PS3) machines.
 
--Michael Dillon
 