2008-03-25 01:17:15 |
this has been, to me, one of the most fascinating nanog
threads in years.
at the moment my own datacenter problem is filtration. isc
lives in a place
where outside air is quite cool enough for server inlet
seven or more months
out of the year. we've also got quite high ceilings. a 2HP
roof fan will
move 10000 cubic feet per minute. we've got enough make-up
air for that.
but, the filters on the make-up air have to be cleaned
several times a week,
and at the moment that's a manual operation.
mechanical systems, by comparison, only push 20% make-up
air, and the filters
seem to last a month or more between maintainance events.
i'm stuck with the
same question that vexes the U S Army when they send the
M1A1 into sandstorms,
or that caused a lot of shutdowns in NYC in the days after
9/11: what kind of
automation can i deploy that will precipitate the
particulates so that air
can move (for cooling) and so that air won't bring grit
(which is conductive)?
--
Paul Vixie
|
|
| RE: rack power question |
  United Kingdom |
2008-03-25 06:23:51 |
> what kind of automation can i deploy that will
> precipitate the particulates so that air can move (for
> cooling) and so that air won't bring grit (which is
conductive)?
Have you considered a two-step process using water in the
first
step to remove particulates (water spray perhaps?) and then
an
industrial air-drier in the second step?
Alternatively, have you considered air liquifiers like
those
used in mining (Draegerman suits) which produce very cold
liquid
air? The idea would be to spray the liquid air inside the
data
center rather than blowing in the gaseous form.
Of course, I don't know if the economics of this work out,
although
there are people working on increasing the efficiency of
air
liquification
so there is quite a bit of price variation between older
methods and
newer ones.
--Michael Dillon
|
|
| Re: rack power question |
  Australia |
2008-03-25 06:52:55 |
This thread begs a question - how much do you think it'd be
worth to do
things more efficiently?
Adrian
|
|
| Re: rack power question |
  United Kingdom |
2008-03-25 07:23:15 |
$5
Adrian Chadd wrote:
> This thread begs a question - how much do you think
it'd be worth to do
> things more efficiently?
>
>
>
>
> Adrian
>
|
|
| Re: rack power question |

|
2008-03-25 07:31:15 |
|
I still think the industry needs to standardise water cooling to popularise it; if there were two water ports on all the pizzaboxes next to the RJ45s, and a standard set of flexible pipes, how many people would start using it? There's probably a medical, automotive or aerospace standard out there.
On Tue, Mar 25, 2008 at 12:23 PM, Leigh Porter < leigh.port er ukbroadband.com">leigh.porter ukbroadband.com> wrote:
$5
Adrian Chadd wrote:
> This thread begs a question - how much do you think it'd be worth to do
> things more efficiently?
>
>
>
>
> Adrian
>
|
| Re: rack power question |
  United Kingdom |
2008-03-25 07:35:53 |
That would be pretty good. But seeing some of the disastrous
cabling
situations it'd have to be made pretty idiot proof.
Nice double sealed idiot proof piping with self-sealing
ends..
--
Leigh
--
Leigh
Alexander Harrowell wrote:
> I still think the industry needs to standardise water
cooling to popularise
> it; if there were two water ports on all the pizzaboxes
next to the RJ45s,
> and a standard set of flexible pipes, how many people
would start using it?
> There's probably a medical, automotive or aerospace
standard out there.
>
> On Tue, Mar 25, 2008 at 12:23 PM, Leigh Porter
<leigh.porter ukbroadband.com>
> wrote:
>
>
>> $5
>>
>>
>> Adrian Chadd wrote:
>>
>>> This thread begs a question - how much do you
think it'd be worth to do
>>> things more efficiently?
>>>
>>>
>>>
>>>
>>> Adrian
>>>
>>>
>
>
|
|
| Re: rack power question |

|
2008-03-25 08:08:05 |
|
A valve in the connector; has to be pushed in by the other connector to let the water flow. Water pressure pushes it shut otherwise so it fails-safe.
On Tue, Mar 25, 2008 at 12:35 PM, Leigh Porter < leigh.port er ukbroadband.com">leigh.porter ukbroadband.com> wrote:
That would be pretty good. But seeing some of the disastrous cabling
situations it'd have to be made pretty idiot proof.
Nice double sealed idiot proof piping with self-sealing ends..
--
Leigh
--
Leigh
Alexand er Harrowell wrote:
> I still think the industry needs to standardise water cooling to popularise
> it; if there were two water ports on all the pizzaboxes next to the RJ45s,
> and a standard set of flexible pipes, how many people would start using it?
> There's probably a medical, automotive or aerospace standard out there.
>
> On Tue, Mar 25, 2008 at 12:23 PM, Leigh Porter < leigh.porter ukbroadband.com">leigh.porter ukbroadband.com>
> wrote:
>
>
>> $5
>>
>>
>> Adrian Chadd wrote:
>>
>>> This thread begs a question - how much do you think it'd be worth to do
>>> things more efficiently?
>>>
>>>
>>>
>>>
>>> Adrian
>>>
>>>
>
>
|
| Re: rack power question |

|
2008-03-25 08:11:37 |
|
It would sure be nice if along with choosing to order servers with DC or AC power inputs one could choose air or water cooling.
Or perhaps some non-conductive working fluid instead of water. That might not carry quite as much heat as water, but it would surely carry more than air and if chosen correctly would have more benign results when the inevitable leaks and spills occur.
Of course, my chemistry is a little rusty, so I'm not sure about the prospects for a non-toxic, non-flammable, non-conductive substance with workable fluid flow and heat transfer properties 
A close second might be liquid cooled air tight cabinets with the air/water heat exchangers (redundant pair) at the bottom where leaks are less of an issue (drip tray, anyone? )...
Less practical but more fun to contemplate would be data centers pressurized with a working gas that offers better heat transfer than oxygen/nitrogen and no oxidation potential. Airlocks and suits for the techs, but no fire worries ever. Heck, just close the room and inject liquid nitrogen under the raised floor to be scavenged overhead and re-compressed, chilled, liquefied and sent round again. Reserve cooling for power outages is just huge dewars full of liquid nitrogen 
Not so serious today,
-Dorn
On Tue, Mar 25, 2008 at 8:31 AM, Alexander Harrowell < a.harrowel l gmail.com">a.harrowell gmail.com> wrote:
I still think the industry needs to standardise water cooling to popularise it; if there were two water ports on all the pizzaboxes next to the RJ45s, and a standard set of flexible pipes, how many people would start using it? There's probably a medical, automotive or aerospace standard out there.
On Tue, Mar 25, 2008 at 12:23 PM, Leigh Porter < leigh.port er ukbroadband.com" target="_blank">leigh.porter ukbroadband.com> wrote:
$5
Adrian Chadd wrote:
> This thread begs a question - how much do you think it'd be worth to do
> things more efficiently?
>
>
>
>
> Adrian
>
|
| Re: rack power question |
  United States |
2008-03-25 08:38:25 |
Once upon a time, Dorn Hetzel <dhetzel gmail.com> said:
> Of course, my chemistry is a little rusty, so I'm not
sure about the
> prospects for a non-toxic, non-flammable,
non-conductive substance with
> workable fluid flow and heat transfer properties
Fluorinert - it worked (more or less) for the Cray Triton.
--
Chris Adams <cmadams hiwaay.net>
Systems and Network Administrator - HiWAAY Internet
Services
I don't speak for anybody but myself - that's enough
trouble.
|
|
| RE: rack power question |
  United States |
2008-03-25 08:46:11 |
|
|
Paul,
Using a multi-stage filter system with the large partical filters in front and an ionizing stage to remove smaller but still large enough particals to cause dust. Clean room filters would be an overkill.
John (ISDN) Lee
From: owner-nanog merit.edu on behalf of Paul Vixie Sent: Tue 3/25/2008 2:17 AM To: nanog merit.edu Subject: Re: rack power question
this has been, to me, one of the most fascinating nanog threads in years.
at the moment my own datacenter problem is filtration. isc lives in a place where outside air is quite cool enough for server inlet seven or more months out of the year. we've also got quite high ceilings. a 2HP roof fan will move 10000 cubic feet per minute. we've got enough make-up air for that. but, the filters on the make-up air have to be cleaned several times a week, and at the moment that's a manual operation.
mechanical systems, by comparison, only push 20% make-up air, and the filters seem to last a month or more between maintainance events. i'm stuck with the same question that vexes the U S Army when they send the M1A1 into sandstorms, or that caused a lot of shutdowns in NYC in the days after 9/11: what kind of automation can i deploy that will precipitate the particulates so that air can move (for cooling) and so that air won't bring grit (which is conductive)? -- Paul Vixie
|
|
|